ManagedAsymmetricEss Coefficient for [ess0,L1,ACTIVE] was not found

Hi Waqar,

You do not write into the SET_ACTIVE_POWER_L1_EQUALS,… channels directly if you implement an Ess. They are write only and used only by controllers. What you have to do is to implement the applyPower()-method. See this post: ESS that can talk with OpenEMS using Modbus TCP - #4 by stefan.feilmeier.

Best regards,
Thomas

2 Likes