I have been encountering a strange issue when testing the implementation of a new ESS device in OpenEMS.
When I have been testing my modbus implementation using the controller FixActivePower, the system setpoints have spiralled upwards away from the ActivePower setpoint that I set.
See below for some excerpts from the debug log - the ‘setpoint’ in the log is the value read from the register where the active power setpoint is written - we are using ManagedSymmetricEss.ChannelId.DEBUG_SET_ACTIVE_POWER to read this.
In the below example I set the ACTIVE_POWER in the controller to -1500. You can see that at every step the ESS reaches the setpoint within the next cycle after the value is written to the register. Therefore it seems like the problem is not to do with how the value is being written with FC16WriteRegistersTask as it seems to move to the correct value for ActivePower.
The strange thing is that it seems like the problem is that applyPower is being controlled with incorrect values - i.e the issue is upstream of my ESS - although maybe the feedback from the ESS is contributing to this.
Has anyone experienced anything like this?
12:18:03.444 — L: 0 W, Setpoint: 0 W
12:18:03.452 — L: -200 W, Setpoint: 0 W
12:18:04.446 — L: -100 W, Setpoint: 0 W
12:18:05.441 — L: -100 W, Setpoint: 0 W
12:18:06.442 — L: -200 W, Setpoint: 0 W
12:18:07.459 — L: -100 W, Setpoint: 0 W
12:18:08.475 — L: -200 W, Setpoint: -1400 W
12:18:09.443 — L: -1400 W, Setpoint: -1600 W
12:18:10.445 — L: -1600 W, Setpoint: -2700 W
12:18:11.450 — L: -2800 W, Setpoint: -1700 W
12:18:12.444 — L: -1800 W, Setpoint: -2700 W
12:18:13.446 — L: -2800 W, Setpoint: -500 W
12:18:14.441 — L: -600 W, Setpoint: -2500 W
12:18:15.443 — L: -2600 W, Setpoint: 700 W
12:18:16.442 — L: 600 W, Setpoint: -3500 W
12:18:17.479 — L: -3600 W, Setpoint: 1700 W
12:18:18.447 — L: 1600 W, Setpoint: -5700 W
12:18:19.448 — L: -5800 W, Setpoint: 3700 W
12:18:20.446 — L: 3600 W, Setpoint: -8900 W
12:18:21.447 — L: -9000 W, Setpoint: 7900 W
12:18:22.454 — L: 7800 W, Setpoint: -14100 W
12:18:23.449 — L: -14200 W, Setpoint: 15300 W
12:18:24.446 — L: 15100 W, Setpoint: -23500 W
12:18:25.448 — L: -23500 W, Setpoint: 27800 W
12:18:26.451 — L: 27600 W, Setpoint: -40100 W
12:18:27.450 — L: -40000 W, Setpoint: 49600 W
12:18:28.464 — L: 49200 W, Setpoint: -69100 W
12:18:29.452 — L: -69000 W, Setpoint: 87700 W
12:18:30.447 — L: 0 W, Setpoint: -100000 W
12:18:31.454 — L: 0 W, Setpoint: 67500 W
12:18:32.451 — L: 0 W, Setpoint: -1500 W
12:18:33.449 — L: 0 W, Setpoint: -1500 W
12:18:35.526 — L: 0 W, Setpoint: 0 W
12:18:36.451 — L: 0 W, Setpoint: 0 W
12:18:37.450 — L: 0 W, Setpoint: 0 W